4.旧防水层大面积脱落,需要铲除重新做防水。![](https://qimg.cdnmama.com/gz/data/attachment/forum/201709/01/1353231enelqzjyjejh9hw.jpg?imageView2/2/w/600/h/0/format/jpg/q/90)
![](https://qimg.cdnmama.com/gz/data/attachment/forum/201709/01/135343qavnor6xgmg6nmzv.jpg?imageView2/2/w/600/h/0/format/jpg/q/90)
5.管线间距过小,少于2cm。管间距过小容易造成后期水泥覆盖时产生空鼓。
![](https://qimg.cdnmama.com/gz/data/attachment/forum/201709/01/135628ggvnrxe8e14ktrr1.jpg?imageView2/2/w/600/h/0/format/jpg/q/90)
这一段间距还好,不过大家也可以看到后面水电管交叉在一起,电管的接口还卡在交叉处呢!(必须整改!)
![](https://qimg.cdnmama.com/gz/data/attachment/forum/201709/01/1356282hkkpubpb40y04tq.jpg?imageView2/2/w/600/h/0/format/jpg/q/90)
这段间距明显太小。
水电现场继续大放送~国庆假期结束,离春节又近了一步,好多麻油都心焦焦地等着春节前搞定装修。心急活可不能急!装修质量和安全性才是第一位~接下来,我们看图说话,来看看水电装修现场还有哪些值得注意的点,自家装修可以防范于未然呢?
![](http://qimg.cdnmama.com/gz/data/attachment/forum/201710/09/172728wkjxeef14fnwmnz7.jpg_thumb.w700?imageView2/2/w/1080/h/0/format/jpg/q/90/)
1.厨房全部翻新改造,水电基本横平竖直(天花走管不规范,未走顶面,走管固定不规范,要求用管卡固定)
![](http://qimg.cdnmama.com/gz/data/attachment/forum/201710/09/172718il56bv20lg4kx4vv.jpg_thumb.w700?imageView2/2/w/1080/h/0/format/jpg/q/90/)
2.顶面木条未拆除,原天花吊筋未拆除,要求拆除,避免后期发霉生虫
![](http://qimg.cdnmama.com/gz/data/attachment/forum/201710/09/181256zpf66f9tg6trr42o.jpg_thumb.w700?imageView2/2/w/1080/h/0/format/jpg/q/90/)
3.总水阀安装不规范,要求安装铜芯水阀禁止安装槊料类总阀;
![](http://qimg.cdnmama.com/gz/data/attachment/forum/201710/09/173853y58yi8mxnccai5aa.jpg_thumb.w700?imageView2/2/w/1080/h/0/format/jpg/q/90/)
4.要求再做一次储水测试;5.厨房吊铝扣天花问题需尽快落实,避免后期产生不必要的增项费用及工期延误风险。